Any WW heating engineers?

I have two zones in my house, one rads and one underfloor heating which were working fine from the old combi boiler, which then failed and needed replacing.

Ever since the new ATAG boiler has been installed we been getting no end of 'flow control' errors, and very little temp in the underfloor.

After many weeks of resetting the boiler and getting the boiler looked at under warranty, the latest guy says the original plumber has done it wrong. And the zone valves should be on the flow leg, and not return as they are; as such the flow and return temps are not as expected so boiler errors?

However, quick google check shows valves can be fitted on either leg, so is he also giving me duff advice?

Do I need to go back to original guy and get him back to do the pipework? Has he done it wrong? And why would this impact on my UFH and not my rads?

Engineer said because normal rads bi-direction but UFH isn't?? Is that correct as there is some heat getting to.floor just boiler is off more that it's on?

Thanks for any advice.

Link to comment
Share on other sites

  • Site Supporter
2 hours ago, JimmyRiddle said:

Any WW heating engineers?

I have two zones in my house, one rads and one underfloor heating which were working fine from the old combi boiler, which then failed and needed replacing.

Ever since the new ATAG boiler has been installed we been getting no end of 'flow control' errors, and very little temp in the underfloor.

After many weeks of resetting the boiler and getting the boiler looked at under warranty, the latest guy says the original plumber has done it wrong. And the zone valves should be on the flow leg, and not return as they are; as such the flow and return temps are not as expected so boiler errors?

However, quick google check shows valves can be fitted on either leg, so is he also giving me duff advice?

Do I need to go back to original guy and get him back to do the pipework? Has he done it wrong? And why would this impact on my UFH and not my rads?

Engineer said because normal rads bi-direction but UFH isn't?? Is that correct as there is some heat getting to.floor just boiler is off more that it's on?

Thanks for any advice.

Zone valves should never be fitted on the return. Google may have sent you to something completely different.

In simple terms, the zone valve decides when and where to send the hot water - without a zone valve on the flow 'leg' it will be sending water to both zones. The priority in this instance will always be hot water to taps/showers and explains why your UFH is getting little or no heat.

Your original guy has made a really really basic error. I mean, worryingly basic.

The pipework is probably fine, but the zone valves need putting in the correct locations - close to the boiler.

DM me if needs be, happy to ring you mate.

 

Link to comment
Share on other sites

  • Site Supporter
1 hour ago, Spider said:

Zone valves should never be fitted on the return. Google may have sent you to something completely different.

In simple terms, the zone valve decides when and where to send the hot water - without a zone valve on the flow 'leg' it will be sending water to both zones. The priority in this instance will always be hot water to taps/showers and explains why your UFH is getting little or no heat.

Your original guy has made a really really basic error. I mean, worryingly basic.

The pipework is probably fine, but the zone valves need putting in the correct locations - close to the boiler.

DM me if needs be, happy to ring you mate.

 

What a top banana answer. Always pays to consult an expert.

Link to comment
Share on other sites

  • 1 year later...
On 22/04/2021 at 12:39, Spider said:

Zone valves should never be fitted on the return. Google may have sent you to something completely different.

In simple terms, the zone valve decides when and where to send the hot water - without a zone valve on the flow 'leg' it will be sending water to both zones. The priority in this instance will always be hot water to taps/showers and explains why your UFH is getting little or no heat.

Your original guy has made a really really basic error. I mean, worryingly basic.

The pipework is probably fine, but the zone valves need putting in the correct locations - close to the boiler.

DM me if needs be, happy to ring you mate.

 

Hi pal, I've just booked to have a hybrid solar system fitted and will need a immersion for the Eddi to feed.  I live in a 2 bed bungalow and there's only me, I'm out all day.  I only have showers so reckon I won't need a huge one.  Can you recommend one for me please, fitted and can be heated solar.  Thank you 😊 

Link to comment
Share on other sites

  • Site Supporter
22 minutes ago, Breightmet Boy said:

Hi pal, I've just booked to have a hybrid solar system fitted and will need a immersion for the Eddi to feed.  I live in a 2 bed bungalow and there's only me, I'm out all day.  I only have showers so reckon I won't need a huge one.  Can you recommend one for me please, fitted and can be heated solar.  Thank you 😊 

Alreet. What size water tank is it going in?

Link to comment
Share on other sites

  • Site Supporter
1 minute ago, Breightmet Boy said:

sorry, I've already got a water tank in 

You’ll only need a 3kW immersion.

Are you getting a diverter to send your solar power to it? iBoost or similar?

is it a vented tank? (Old copper unit in a foam jacket)

Link to comment
Share on other sites

16 minutes ago, Spider said:

You’ll only need a 3kW immersion.

Are you getting a diverter to send your solar power to it? iBoost or similar?

is it a vented tank? (Old copper unit in a foam jacket)

I've not bought one yet, waiting till nearer they install the solar.  Yes, I've bought a Eddi to divert to the tank when the battery is full.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.